Latch/Lock Default Values vs. Echo

Just a little thing we stumbled across today, in our space with both Sensor3 racks with ThruPower modules and Echo relay panels, where we're starting to make use of Latch/Lock mode on both.

At least in our space, the Sensor3 Thrupowers in Latch/Lock were set to ON @ 41-50, OFF @ 81-90. Conversely, the Echo relays in Latch/Lock were set to ON @ 81-90, OFF @ 41-50. Not sure if this is a system default or a byproduct of how our space was commissioned, but it did leave us scratching out heads for a fair few minutes. Thought it might be worth mentioning for anyone else troubleshooting Latch/Lock down the road.