How reliable would my 3000' long universe be with 11 of these controllers with a maximum distance between being 325feet.
Has anyone done this?
We would put a network switch at each junction.
andrew
How reliable would my 3000' long universe be with 11 of these controllers with a maximum distance between being 325feet.
Has anyone done this?
We would put a network switch at each junction.
andrew
The standard for ethernet over copper wire is 100 meters/ 300' max. Fiber optic cables go much further. So long as each section is under that you should be fine. There is a limit on how many switches one can string, but I think you are well under that line, AFAIR