Replacing Halogen Bulbs with LED Bulbs

Our maintenance staff want to replace all of the halogen bulbs in our auditorium can lights with LED bulbs. We have the house lights on the same Sensor racks as our theatrical lighting and we control it all with the Paradigm system and an ETC ION control board.

Can they work well? Do you recommend a certain brand or style? Are there any risk to the dimmers themselves?

The LED's do say dimmable but I know we would have to work on the dimming curves to get the most out of them.

Any help would be appreciated

  • LED bulbs may be dimmable but the dimming characteristics near 0% may be undesirable for house lights. Most replacement dimmable LEDs will flicker and/or abruptly produce no light once the voltage drops below a minimum level. Those that avoid this while dimming down will still "pop" on when dimming up. It's very much a try-before-you-buy situation.

    The TCP brand seems to be getting good reviews on controlbooth.com.

     

  • Unfortunately there aren't any easy answers when it comes to LED replacement lamps.  We've seen that even different lamp models from the same manufacturer can behave completely differently, so it's impossible to make any accurate generalizations.  The only way to know for sure how a specific product will perform is to test it. 

    If you have a product in mind that you're looking at using, your best bet is to send an email with the details of the lamp and your system to aesupport@etcconnect.com to check whether it's one that's been tested before.  If not, then we may ask that samples be sent in for testing.

     

  • This is happening to me too; slightly different system though so take my results with a grain of salt, test for yourself. 

    Sensor Racks, ETCNet2 & sACN both control via Cobalt-on-Congo and Legacy Unison. The  http://www.tcpi.com/spec-sheets/ELITE/Designer-Elite/Designer-Elite-DIM-PAR-Series_print.pdf is what we liked* in a PAR38 size, and my local tech support guy allows as how it's one of the least horrible options he's seen. (He estimates his clients getting this kind of request a couple of times a month, these days.) The fade got down to about 6% before dropping out: if they pull the trigger on this purchase I'll try to create a custom curve for them from the desk. No perceptible flicker, and we tested without the existing diffuser lenses in place. However: we did see them briefly stick on at the bottom of a 5-second fade, couldn't duplicate it, but it does indicate caution. The whole circuit behaved as one, no popcorning within the bank of 12, but I wouldn't want to rely on the idea the whole roomful wouldn't do the same thing unpredictably and probably not in unison. In concert. Simultaneously. 

    *By "liked," honestly, what I mean is "was surprised to not completely hate."  Building a fade that is more immediately perceptible to the audience--steeper at the top, I think--will be a challenge. I'll fling an email at the pros for more input, but my only other concern right now is the potential for camera flicker in casual video shots. If we light the audience specifically for IMAG, I'm sure we'll put tungstens on them, but I'm not sure without that there might not be a problem.  Hope it helps.

     

  • Thank you all. Very helpful. We are going to isolate one circuit, replace those lamps with the TCP bulbs, work on the dimming curves and see if it will give us acceptable results.

  • Please repost your results!  There are a lot of interested parties!  Thanks!

  • Do a slow out, say 20 count, as well as 5 or so. Same counts coming up.

    Video the results and post.  

  • Video is problematic for this sort of thing. This is especially true with most people's default video device: their phone. The automatic exposure adjustments will try to compensate for the changing light levels as you dim and the resulting video will be very misleading at best.

    Even a good camera that allows for manual control may still fail to show things that your eye would pick up, or may show things that are imperceptible to the eye. 

    It turns out that finding a way to objectively assess dimming performance is a pretty difficult task to accomplish.

  • I have been using TCP Elite Designer series lamps and it is touch and go with these. They work well one day and then they flicker another. I have a Sensor 3 rack and have tried different things but so far I have resorted to having to install an incandescent on the circuit to get them to perform well. Not fun when you have over 40 sections of track and I have to put a fixture in the corner with a 15w bulb and cover it with black out wrap.

    So even testing (which I did before I purchased) is not 100% fool proof.
  • Are you using a D20 module to dim the TCP lamps? If that's the case, and if adding an incandescent lamp to the circuit improves performance, then there may be one more setting to try: increasing the Zero Cross Blanking Time. This is in a special configuration menu*, so you'll want to give phone support a call and have them walk you through changing it.

    (*It's a rack-wide setting and adjusting it improperly can have negative consequences for other circuits, so it's not part of the general config.)
  • Same story here -- and I have a series of sconces that have to remain on at a low level for fire egress lighting. Last week my incandescent bulb burned out in the middle of a show and the sconces all bumped to 100% intensity. I was horrified. I'm going to have to put two incandescent or halogen bulbs in each line just in case.

    First world problems, but annoying nonetheless.