I'm having trouble with with dimmers 25>40 on my 48x2.4k Sensor Touring Rack with classic CEM. The dimmers are giving 100% output at 1%.
I have done the following troubleshooting:
-Confirmed that all dimmers in the rack are D20 dimmer cards.
-The CEM is set for SP24.
-Confirmed linear dimming curve and that all other attributes are normal at rack, no change.
-Confirmed linear dimming curve at console (Hog 4 Full Boar, patched as standard desk channels), no change.
-Swapped CEMs, no change.
-Swapped Dimmer Modules, no change
-Called up channels manually from rack, same result - 100% output while asking for 1%.
I have re-patched the channels that were on dimmers 25>40 to the remaining dimmers on the same rack using the same socapex circuits and everything functions properly. With the exception of 25>40.
All of this leads me to believe that its an issue with the internals of the rack, maybe some control board. I've read in other forums that there could be an issue with phasing being mismatched. Dimmers 25>40 are on the L1 and L2. However, I am hesitant to believe this is my issue. If it was a phasing issue, shouldn't I see the same issue with the rest of the dimmers on those legs?
Thoughts?
Thanks.