Replacing Workers with LED

Hello,

We currently have Sensor CEM+ with both dimmer and relay modules.

We are looking to replace our working lights, that no longer work.


Currently they are Fluorescent Tubes through ballast using the Relay Modules. There are for workers only so ON/OFF function.


We would like to know if it matters what we replace with it, whether its new Fluorescent with Ballast, Fluorescent with Starter or LED Fluorescent equivalent. 

Is there a reason for the Sensor not to have one of the mentioned units?

Parents
  • Hello,

    As you are keeping the the replacement working light on relay modules, you will be fine so long as you:

    A) Remain under the modules rated load (see module datasheet).

    B) Compile with local electrical regulations.

    Datasheets can be found at http://www.etcconnect.com 

  • Thanks, was just making sure we were not missing something. The power rating will be far less if replaced with LED in the same quantity of bulkheads.

    Will be installed by electricians so no issue there.

    Thanks for your help
Reply
  • Thanks, was just making sure we were not missing something. The power rating will be far less if replaced with LED in the same quantity of bulkheads.

    Will be installed by electricians so no issue there.

    Thanks for your help