I have a faulty circuit. The system is comprised of:
ETC SR 48 rack 12 years old
Kleigl raceways 32 years old
For the purpose of testing, I inserted a CC20 module
We are working with circuits 47 (good) and 48 (bad)
The GAM Check reads Hot / Ground Reversed
The stagepin pigtail is wired correctly: BK / W / G
The batten junction box looks correct. There is no real pattern for the various repeating colors from the multi cable.
Circ 47 GAM checks and meters fine and normal. H to N=120v, H to G=120v, N to G= ~
Circ 48 GAM checks and meters with a fault. H to N=94v, H to G=123v, N to G=26.5v
Anyone have an idea as to how I fix this?