Smart Module2 dimming output
Hello . . .
we have a strange problem that maybe someone has seen before
we are using a SM2 in a FOH position for 4 S4 575s ... when two of the channels are on (@ FULL) they seem fine .. when we add the other two channels we notice that the output of the first two channels dims a bit . . .  not much .. but enough to notice
mathematically we are within the wattage ratings for the SM2 and nothing is tripping . .
they are getting power from a CC20 card and not a dimmer parked or set to switched or non dim . .
any ideas?
  • Hello,
    I think what you are experiencing here is voltage drop due to an increase in current. U=IR
    For example, if we have a U of 110v at the Sensor module, and a 100ft (30m) run of AWG14 (2mm_2) to the SM2.
    AWG14 has a resistance of 2.525Ω/1000ft. (2.525/1000)*100=0.2525Ω for a 100ft run.
    Combine this with an assumed internal resistance of 0.2Ω with in the SM2, we get R=0.4525Ω
    We already know the wattage of the fixtures, and as they are purely resistive loads P=IU or I=P/U.
    With two S4 we have I=(575x2)/110 = 10.455A
    With four S4 we have I=(575x4)/110 = 20.91A
    So combining this all together, the voltage drop with two S4 is:
    U=IR=10.455x0.4525=4.731v or roughly 94.8% of full
    with four S4:
    U=IR=20.91x0.4525=9.462v or roughly 89.6% of full
    In reality there are many more factors to take in to account, but this does demonstrate the effect of current on a single circuit to the perceived light output.
    (N.B. The above values are for example only, and I normally work in metric!!)
    Regards,
    Marcus