Backstage lighting control system on the fritz

I recently came into managing a high school theater that is used frequently for community events.  As typical, the school district has no interest in expenditures for maintaining the facility.  While it's a nicely designed and equipped theater, the joke in the community is how half the gear in it doesn't work.

The ETC Express 24/48 controller and stage lighting system work just fine.  What doesn't work right is what appears to be a custom ETC backstage/orchestra pit/catwalk lighting system as seen in one of the attached pictures.  When energized, at least some of the zones turn on and off on their own accord.  Everyone says "all" of the zones do this, but I have not yet confirmed that to be the case.  The district electrician says he doesn't know what the problem is and can't be bothered with additional request for fixing this.

I have also noticed that some of the multi-button wall switches work correctly and others don't.  That is, the ones that work correctly appear to toggle correctly since the indicator lamp turns on or off when the button is pressed.  Ones that don't work correctly don't change indication when the buttons are pressed, or when one button is pressed, a different or even multiple other  indicators go on or off on the wall plate.  Our wall plates vary from 2-button on up to 5-button models.

My question for anyone familiar with this system and repairing it is, does this random light switching happen because of faulty wall switches?  Or are the wall switches faulty because the controller module they are connected to is faulty and the random switching switching also happens because of the faulty controller module?

Any tips that can help pinpoint the issue will go a long way in getting repair parts and our electrician to get things fixed.

Thanks.

Parents
  • It is going to be hard to get to the bottom of much without looking at the ETC job prints which will have the wiring schematics for the stage management panel. Calls to ETC support cost you nothing and we will likely be able to figure out your job number based on city, state and name of facility.

    800-688-4116

    NOTE: if you do not have access to a lot of areas, it will be hard to troubleshoot. You will need to find the dimmer room which will most likely also have the architectural processor.

  • Thanks for all of the replies.  I'll have to come up with some time to reach out to ETC, but even without prints there have to be ways to troubleshoot to nail down the issues.  The problem is not with any of the house dimmers or controls.  The problems are with this section of the controller.

    As I've pieced together, it appears that the yellow buttons are momentary and they toggle the state of the switching logic on the circuit boards to which they are attached which then energizes the appropriate relay upstairs.  Toggling the state of the switching logic is also what the unison wall buttons do.  If you sit and watch these yellow buttons, you'll see some light up or go dark all by themselves and of course the circuit they control also turns on/off.  Specific areas I know of that switch randomly are at least two of the three orchestra pit circuits and one or more up in the catwalks.

    Take the orchestra pit.  My gut says to disconnect the malfunctioning Unison wall switch and see if the random switching continues.  If it does, then I would try swapping the logic board with an identical one that I haven't seen the issue occur and see if the random switching now moved to other zones.  But, of course I was hoping someone here had experience with this sort of problem and could offer a suggestion that would target us to the solution because any other scenario requires enough labor to make getting help difficult.

    Thanks for everyone's suggestions again.  Yes, I do see the value in getting schematics and will make an effort to obtain them.  It's just frustrating to have great equipment in the facility that is broken and no one seems to care enough to make it right.

  • IM me the name and address of the facility and I see if I can find the prints.

    You seem to indicate that the stage management panel switches output wires that go up though a conduit to a relay panel for direct control. Maybe they do but that would not be the norm for and ETC system based on what I’m seeing on the panel. ‘Normally’ the local switches would be wired to a local Unison contact interface station with a local power supply. The switch closures on the interface station would be translated into the Unison control protocol and get sent to the Unison processer. From there the data would control Sensor dimming racks, Unison dimming racks, and/or a DMX control relay rack.

    Undo the screws on the front of the stage management rack and pull the panel out (or the rack might fully swing open to see the backside of everything). Look to see where the wires from the switches go. I’m guessing they go to a terminal strip and that the terminal strip is wired to a Unison contact interface station.

    Once again, IM me the name of the facility and the address and I’d likely be able to tell you exactly how it is all wired.

    Mike Meskill

    Global Technical Service Manager

    ETC

Reply
  • IM me the name and address of the facility and I see if I can find the prints.

    You seem to indicate that the stage management panel switches output wires that go up though a conduit to a relay panel for direct control. Maybe they do but that would not be the norm for and ETC system based on what I’m seeing on the panel. ‘Normally’ the local switches would be wired to a local Unison contact interface station with a local power supply. The switch closures on the interface station would be translated into the Unison control protocol and get sent to the Unison processer. From there the data would control Sensor dimming racks, Unison dimming racks, and/or a DMX control relay rack.

    Undo the screws on the front of the stage management rack and pull the panel out (or the rack might fully swing open to see the backside of everything). Look to see where the wires from the switches go. I’m guessing they go to a terminal strip and that the terminal strip is wired to a Unison contact interface station.

    Once again, IM me the name of the facility and the address and I’d likely be able to tell you exactly how it is all wired.

    Mike Meskill

    Global Technical Service Manager

    ETC

Children
No Data