I am coming out of DMX B of the an ERn and going to a Lyntec LCLC 314 panel, that is able to use dmx.. Has anyone tried this, or have any ideas how to make it work to trip the circuits in the Lyntec panel. I have had nothing but bad luck.
I am coming out of DMX B of the an ERn and going to a Lyntec LCLC 314 panel, that is able to use dmx.. Has anyone tried this, or have any ideas how to make it work to trip the circuits in the Lyntec panel. I have had nothing but bad luck.
I'm assuming we're talking about Paradigm LightDesigner configuration here (rather than Light Manager) since you mentioned an ERn. If that's correct, you would want to set the Lyntec to use whatever addresses on DMX output B that you patched the relevant channels into. If it's Light Manager, then the Lyntec settings should correspond to the relevant dimmer numbers from the zone properties.
Thank you.. and yes I am using Pardigm LightDesigner in this situation. I sure hope this works
I see you're located in Maple Grove, MN. If you'd like some local support, give us a call.
Mike Watson
Gopher Stage Lighting - 612-871-0138
Thanks every one for your comments it helped. I was able to get everything I needed to work the way they wanted it. Yes the company I work at is in Maple Grove. Only part about the job was, it was in Tennessee. But if I have lighting questions I will give you guys a call to see if you know a solution.