connect congo to datagate mk2 entecc by artnet

I can not connect the console to Datagate
it drives me crazy, can someone help me?

desk ip: 10.101.81.101 / gateway 255.255.0.0 and 255.255.255.255 (I tried the 2 options)
Artnet: 255255255255/10255255255/2255255255
I tried the three possibilities.


on the Datagate:
IP: 10.101.50.101 / gateway: 255.255.255.255

When do I start the console, it shows me the ip though the console and artnet (top right) but nothing comes out.

Of course, I will restart each time the console that I have changed a setting.

Thank you in advance,

Xavier

Parents
  • What IP settings do you have for each?

    There are three IP settings for the Congo Console and the "Datagate":

    • IP Address
    • Subnet Mask
    • Gateway IP

    A subnet mask of 255.255.255.255 will never work, you usually want "255.255.0.0"

    Then in the Congo Art Net settings you want either "255.255.255.255" or "10.255.255.255" as the Artnet Address.
    - The first number is either 255 or should match the first number in the IP address of the Datagate.

    Congo sends broadcast Art Net 1 for maximum compatibility.

    Secondly, Art Net universes count from 0-0, Congo Universes count from 1. Confirm that you're actually sending the universe you want.
    - By default, to patch to Art Net universe 0-0 you must patch to Congo Universe 1.

    Unfortunately I can't really help you much with the Datagate end, I've never used one of those.

  • thank you for your prompt reply,

    If I understand correctly, the IP address of Datagate must begin with the same address as the address of artnet (10.XXX or 255.XXX)

    currently on the console :
    Console IP: 10.101.81.101
    subnet mask: 255.255.0.0
    Gateway: 10.101.81.101

    Should i put the ip in automatic? or dhcp?

    on the Datagate:
    IP: 10.101.50.101
    subnet mask: 255.255.0.0

    artnet adress: 255.255.255.255
    I should try to 10,255,255,255?

    What is hard is that you restart each time the console, and there is nothing to know if the problem comes from the console or Datagate

    Thanks,

Reply
  • thank you for your prompt reply,

    If I understand correctly, the IP address of Datagate must begin with the same address as the address of artnet (10.XXX or 255.XXX)

    currently on the console :
    Console IP: 10.101.81.101
    subnet mask: 255.255.0.0
    Gateway: 10.101.81.101

    Should i put the ip in automatic? or dhcp?

    on the Datagate:
    IP: 10.101.50.101
    subnet mask: 255.255.0.0

    artnet adress: 255.255.255.255
    I should try to 10,255,255,255?

    What is hard is that you restart each time the console, and there is nothing to know if the problem comes from the console or Datagate

    Thanks,