There are running 2 DP2000 (these are running perfectly)
I’ve recently linkt up a DP8000, and want to test this device.
The DP8000 was running V3.0.0, I forced the DP8000 to load the V3.0.5 software by pressing the 3 buttons at once while powering the device. This works perfect.
The DP8000 is running V3.0.5 (shown in the control panel Hog 3V3.0.5(b2482))
The DP8000 loads the new software but I don’t can get it running.
The display on the DP8000 shows: Connecting, No server, scanning port 6600. 4 The LED near Hog-Net Link is flashing
On the back of the DP8000 the Link LED is on, and the Traffic LED is flashing. (Hog-Net Gigabit – Ethernet)
When you upgraded your IPC did you install the IPC_DP8K app? With out this your DP8K will NOT get the software from the ipc. Also set your iPC to run dhcp and then restart your desk. Reboot and launch a new show then upgrade.
Sounds to me like the 8k app is missing. Upgrade from the hog ipc configuration panel - upgrade it as you would upgrade 3PC.
When you upgraded your IPC did you install the IPC_DP8K app? With out this your DP8K will NOT get the software from the ipc. Also set your iPC to run dhcp and then restart your desk. Reboot and launch a new show then upgrade.
Sounds to me like the 8k app is missing. Upgrade from the hog ipc configuration panel - upgrade it as you would upgrade 3PC.