Cyberlights on 110V?

Hello all
I'm currently working on building up a good set of equipment for my attempt at lighting design. After reviewing many options for used equipment (And my parents demanding for me to buy American made) I've recently discovered the Cyberlight classic as a good choice. However, this brings up my nightmare, in that Cyberlight classics do not support 110V, which I will primarily be dealing with. This also applies to various other lights too, from various manufacturers.

I am curious if anyone knows of any way to get Cyberlights to work on 110V, even though they do not naturally support it. Preferrably, an easy, simplistic way, that won't cost more than the lights themselves to do. I've already looked all through the manual for the Cyberlights, and I understand about their 208/240V Support. So, is there any way to do this that is not unnaturally dangerous, or overly skilled/expensive?

Also, I'm quite curious if anyone knows why the Cyberlights and certain other fixtures from various manufacturers require 200+V, whereas other lights that use the same lamp and same features do not. I'm just curious on that.

Please do let me know! I am really hoping to be able to use High End systems equipment in time, but this nasty roadblock popped up and I must find a way around it to do so.

-C
Parents
  • It must be a cord-connected transformer, listed as cord connected (and not a permanent install transformer with a connection cord added in the field), with properly rated connectors on both input and output. It also has to be properly rated (or appropriately de-rated) for the power factor and harmonic content of the fixture being connected. Ensure that it's setup for a US style grounding scheme, and not a 55v/55v center tapped configuration often used on jobsites in the UK and elsewhere.

    If all of these conditions are met, then there is no problem.


    Bingo! We have a winner!


    Here's the problem: You can't tell from looking at a standard outlet if it's being fed by a 15 amp or a 20 amp breaker. Thus, to be safe you have to assume it's on a 15 amp circuit.

    If a qualified person can determine it's a true 20 amp service, with no other loads connected, than you can draw 15 amps continuously and stay within the strictures of code (at that point the 15 rating of the standard US style power outlet would become the limiting factor since it's less than the 16 amps you can draw from an 80% de-rated 20-amp service)


    And silly me, I always thought having a 10 second peek in the panel to see what breaker size was feeding a circuit was a simple thing to do . . .

    Also, for a Cyber, in this case, per your prior messages pulling 1400 plus step-up transformer losses, you are still well within the 1800 rating of a 15A outlet, and well below the 2400/derate 80% of a 20A breaker . . . .

    I *DO* think these things through . . . . .

    - Tim
Reply
  • It must be a cord-connected transformer, listed as cord connected (and not a permanent install transformer with a connection cord added in the field), with properly rated connectors on both input and output. It also has to be properly rated (or appropriately de-rated) for the power factor and harmonic content of the fixture being connected. Ensure that it's setup for a US style grounding scheme, and not a 55v/55v center tapped configuration often used on jobsites in the UK and elsewhere.

    If all of these conditions are met, then there is no problem.


    Bingo! We have a winner!


    Here's the problem: You can't tell from looking at a standard outlet if it's being fed by a 15 amp or a 20 amp breaker. Thus, to be safe you have to assume it's on a 15 amp circuit.

    If a qualified person can determine it's a true 20 amp service, with no other loads connected, than you can draw 15 amps continuously and stay within the strictures of code (at that point the 15 rating of the standard US style power outlet would become the limiting factor since it's less than the 16 amps you can draw from an 80% de-rated 20-amp service)


    And silly me, I always thought having a 10 second peek in the panel to see what breaker size was feeding a circuit was a simple thing to do . . .

    Also, for a Cyber, in this case, per your prior messages pulling 1400 plus step-up transformer losses, you are still well within the 1800 rating of a 15A outlet, and well below the 2400/derate 80% of a 20A breaker . . . .

    I *DO* think these things through . . . . .

    - Tim