Controlling a Sensor Rack w/ CEM+ via Net3

I have a Sensor Rack w/ a CEM+ and I'm wondering if I can control dimmer levels via Net3 or do I have to run a DMX signal from a node?

 

Thanks,

Mike

Parents Reply
  • One more thing to add, even if you do have a reasonably up to date version which accepts sACN, you may still need to ensure that the patch is correct within the processor. DMX inputs and sACN inputs can have different patches. I have seen systems installed where the DMX patch has been customised but the sACN patch left as 1 to 1 as the engineer didn't expect sACN ever to be used.

     