Relay on cem+ rack

I have 4 ESR36 Racks with CEM+ Modules running software version 3.1.2.9.0.38

I have a number of ER15 modules 

Some are older eg P/N 7070A2105 S/N245292

Some are newer eg  P/N 7070A3305.  S/N 318184

All of the relay modules work in rack 1, 3 and 4

However only the newer modules work in rack 2 

I'm at a loss as to why this is 

I have spoken to a few folks at etc nobody seems to be able to solve this 

All racks installed at the same time (2011 I believe)

All racks are on the same group and same network 

Can anyone help with this?  

Thanks 

Phil

Parents
  • So, there is a solid internal ETC discussion about this.

    Question:

    • What does the sticker/label on the bottom of the module say for both modules?
      • Just in case both are "ER15" on the front but actually a little different
      • (recently ran into this with ELV10 modules where the front label was ELV10 but the bottom label was ELV10-S and the module was wired as a -S)
    • What does the PCB sticker/label say for both modules? (including Rev & S/N) [old vs new]
Reply
  • So, there is a solid internal ETC discussion about this.

    Question:

    • What does the sticker/label on the bottom of the module say for both modules?
      • Just in case both are "ER15" on the front but actually a little different
      • (recently ran into this with ELV10 modules where the front label was ELV10 but the bottom label was ELV10-S and the module was wired as a -S)
    • What does the PCB sticker/label say for both modules? (including Rev & S/N) [old vs new]