Voltage Drop After Plugging In Load

Hello,

On a TV show in NY.   I have 2 stages, each with 400+ sensor dimmers.  On certain channels voltage is measured at output as 122 VAC.  After applying a load (2000watts)  output voltage was measured at 93 VAC.  this only happens on particular channels with no apparent pattern.

Seen this before?  Am in the process of ruling out Dimmer Trays and checking rack setup.   Channel is not profiled in ION

Parents Reply Children
  • Note that they are setup under Basic/Portable rack setup.   I  think I have to change them all to Full Feature to access the Scaling feature.  True?  And under Basic/Portable is there a default output for dimmers.  115vac possibly?

     

  • Yeah, I think you'd have to change them to full feature.  I know Basic/Portable removes a lot of configuration options.

     

    Good luck.

     

  • Ted:

    So the math is in the right range for voltage drop if starting at 115v. We went throughout this, as well. Last season it would be most apparent when putting hard-line blondes next to those that were dimmed through the outlets, or when running 20ks through dimmers using 220v lamps instead of 208v, when next to a hard-patched 10k. The 10ks color temp made them appear much brighter, but good luck getting KAS to switch those for you.

    I set all the racks as full feature, and then networked (that was 13 racks on Stage G). They also ran on sACN. This offered several advantages, key among them:

    You could adjust the scale voltage for the whole system using Web Connect. It is pretty painful trying to do it in the CEM+ for 13 racks/450 dimmers.

    Also with the racks networked and using sACN, you could change the scale voltage settings from the Ion "About" screen. This would give you a chance to "see" the changes from the console, or do an A/B test with someone standing at the light and you in your chair rather than bent over the CEM+. Going from 115v to 125v certainly helped, but still not possible to get 120v on those socapex runs, except when KAS runs really hot. Some days I would come in and the racks were reporting 130v on each phase.

    Of course with the hard-line lights getting brighter with the higher voltage as well, you end up chasing your tail. I lobbied hard to stop using hard line stuff (with 900 dimmers between the stages you would think there wouldn't be a need), but as you know that sounds easier than it actually is.

    James

     