Hi friends,
System details first:
*Sensor permanent installation rack Model SR48 Series.
*2 racks of 96 dimmers each, which appear to be ETCLink-ed because you can access information about dimmers in one rack from the other.
*CEM is labeled "Sensor" on Reset, it says it's a Sensor CEM 2.14.
Problem:
*A pair of dimmers not responding which are in the same card (67 & 68).
*When I scroll to those dimmers in the "About" menu, Dimmer 67 says "No Dimmer"; 68 says "50A Non Dim" (though at the beginning of the troubleshooting process, it also said "No Dimmer" but now it thinks it's a "50A Non Dim", which I suppose would explain why it thinks 67 does not exist. It thinks there is a module with one 50A dimmer instead of 2 20A dimmers)
*I have swapped dimmer modules with ones in slots that are ok and the problem stays local to Dimmers 67 & 68.
So...Can you help me to figure out why the CEM's are misinterpreting this slot?
Much thanks,
Deanna Fitzgerald