Hello,
I have a Echo touch, this is directly connected to my Echo Access.
The problem is that if i connect to my Access, there is no spaces found to control.
Is there something i forget?
Hello,
I have a Echo touch, this is directly connected to my Echo Access.
The problem is that if i connect to my Access, there is no spaces found to control.
Is there something i forget?
Hi Corey,
The Echo Acces is directly connected to the Echo Touch with the black and white cable (ETCConnect).
They both are feed by own 24v power adapters.
I've created spaces on the echo touch.
Which Echo Bus Power Supply for EchoConnect data do you have ?
This is different from the 24VDC AUx power connection.
On the back of EchoAccess Station is a connection for 24VDC Aux Power and below a second connection for EchoConnect. U need a separate ETC EchoConnect Power Supply for this.
24VDC Connection on EchoTouch should not be connected to ECHOConnect connection on EchoAccess Station.
24VDC Aux power is one type of connection and can only be connected to other 24VDC Aux Power connections - these need to be then connected to a 24VDC Power supply.
EchoConnect Bus is another type of connection and can only be connected with other EchoConnect connections - these then need to be connected to a separate official ETC EchoConnect Data Bus power supply.
Please review the EchoTouch, EchoAccess and Echopower Supply Installlation Guides.
24VDC Connection on EchoTouch should not be connected to ECHOConnect connection on EchoAccess Station.
24VDC Aux power is one type of connection and can only be connected to other 24VDC Aux Power connections - these need to be then connected to a 24VDC Power supply.
EchoConnect Bus is another type of connection and can only be connected with other EchoConnect connections - these then need to be connected to a separate official ETC EchoConnect Data Bus power supply.
Please review the EchoTouch, EchoAccess and Echopower Supply Installlation Guides.