v1.4.1 bugs/queries and other suggestions
Hi there - just a few things I've noticed with v1.4.1
-Highlight: Seems to not work correctly if you type [clr enter] while chans are selected.  Doesn't seem to adversely effect highlight operation if you type [clr enter] with no chans selected
 -Rem-Dim: I sometimes use this to go thru chans 1 by 1 to adjust positions of moving lights, however as soon as you press [next] to go to the next channel, and adjustments just made are lost and the fixture returns to the data recorded in the pallet/preset.  Creature or feature?
-Direct Selects on ION: I often open these in the CIA, however as soon as I press [displays] to access the param selection, I then have to re-open the direct select module from the browser.  It would be really nice if there was a way to be able to access the D/S more quickly, or have them repost to the CIA......  I have thought about placing the D/S above the chan info, however my touchscreen and 2nd monitor are of different resolutions and so as a result, if I press [swap] one screen is displaying a whole lot of blank space, and the other screen doesn't fit the whole display
-Update: I recalled a fixture from a particular cue, and then made some adjustments and went to update these changes into a preset.  The preset already contained focus info, but not iris and edge.  At this point the iris, edge, and focus data was all manual (red).  [update preset # enter] only stored the focus data and not the edge or iris info.  Work around was to make the data absolute and then update the preset.  Should I have expected this behavior?  The iris and edge info were previously stored in beam pallets, however once recalling them and then making manual changes I would have expected that an [update preset] command would have captured the manual info
-I have a bunch of HighEnd Studio Spot 575 CMY fixtures and noticed the recent addition of Iris Mode parameter.  I added a value to the Home Preset for this parameter, however if I send the fixture home, the Iris Mode doesn't go to it's home value.
-One suggestion: When updating presets and pallets, I usually place the lamps in the preset I wish to update, make my changes, and then update the preset/pallet.  What I find at the moment is that I have to enter the preset/pallet number, make the changes, and then enter the number again when entering the update command.  Would it be possible to be able to just type [update preset enter] and have the console automatically post the number to the command line by using the last target that was selected.  At present if I try the [update preset] syntax it will post the last target I updated, not the last one that was recalled from.  I have recently started using the direct selects and this does make it a bit easier, but see point above for why this can be a bit frustrating
I'm sure you are probably aware of some of these points already, but I have listed them anyway just incase.  Keep up the great work - I'm loving the new software
Cheers
  • Just to add to the above....
    -Occasionally I get a syntax error when lamping off fixtures
    -Trace Trace, which as I understand is suppose to trace an update as far back as possible in the cue list, doesn't appear to be functioning
    -Iris Mode: I want the iris mode to change 6 seconds into the cue, so I put a delay of 6 on the iris and iris mode parameters, however the Iris mode is still changing at the top of the cue
    -Effects: I have a linear effect running on a group of chans.  the effect is set to cascade - fade by size with a grouping of 7.  On its first cycle some of the chans that are grouped together don't come up, or are slow in coming up.  Subsequent cycles, the chans are coming up when they should be.
    -Fader Control - Rate: What is the current situation with being able to speed up or slow down a cue?  Last I heard, rate wasn't working correctly.  Also, how does one affect the rate on the master playback pair?  Do you use the rate softkey under "fader control" or is the master pair constantly set to be a rate override (as far as I can tell the latter is the case, but a bit of info would be useful as this caused a show stop this evening)
     Thanks once again!
    Cheers
  • BrentFJ:
    -Highlight: Seems to not work correctly if you type [clr enter] while chans are selected.  Doesn't seem to adversely effect highlight operation if you type [clr enter] with no chans selected.  WILL LOOK INTO THIS.  SORRY NO DESK AT THE MOMENT.
     -Rem-Dim: I sometimes use this to go thru chans 1 by 1 to adjust positions of moving lights, however as soon as you press [next] to go to the next channel, and adjustments just made are lost and the fixture returns to the data recorded in the pallet/preset.  Creature or feature?  YEP, AT THE MOMENT, REM DIM IS JUST  A TOGGLE STATE.  YOU CAN'T ACTUALLY MAKE CHANGES TO VALUES AND THEN REVERSE THE REM DIM MODE.  WE'VE DISCUSSED CHANGING THIS, BUT WERE HOLDING OFF UNTIL WE COULD EVALUATE HOW HIGHLIGHT/LOWLIGHT MIGHT IMPACT HOW PEOPLE ARE TRYING TO USE REM DIM.
    -Direct Selects on ION: I often open these in the CIA, however as soon as I press [displays] to access the param selection, I then have to re-open the direct select module from the browser.  It would be really nice if there was a way to be able to access the D/S more quickly, or have them repost to the CIA......  I have thought about placing the D/S above the chan info, however my touchscreen and 2nd monitor are of different resolutions and so as a result, if I press [swap] one screen is displaying a whole lot of blank space, and the other screen doesn't fit the whole display  IN WORK.  LOOKING TO LOCK ANYTHING POSTED IN THE CIA, SO THAT IF YOU DO SOMETHING THAT NEEDS TO BE POSTED TO THE CIA, WHAT YOU HAD BEFORE COMES BACK WHEN YOU CLEAR THAT STATE.
    -Update: I recalled a fixture from a particular cue, and then made some adjustments and went to update these changes into a preset.  The preset already contained focus info, but not iris and edge.  At this point the iris, edge, and focus data was all manual (red).  [update preset # enter] only stored the focus data and not the edge or iris info.  Work around was to make the data absolute and then update the preset.  Should I have expected this behavior?  The iris and edge info were previously stored in beam pallets, however once recalling them and then making manual changes I would have expected that an [update preset] command would have captured the manual info  YEP.  WE CHANGED THE CODE IN 1.3 SO THAT UPDATE WOULD NOT ADD ANYTHING TO A REFERENCE UNLESS SPECIFICALLY REQUESTED.  THAT WAY, YOU COULD HAVE A BUNCH OF MANUAL STUFF ON STAGE AND NOT WORRY ABOUT GETTING UPDATE INTO A SINGLE REFERENCE BY MISTAKE. SO, IF YOU WANT TO ADD IRIS, EDGE AND FOCUS, YOU HAVE TO SPECIFY THAT.  [IRIS, EDGE FOCUS UPDATE TARGET]
    -I have a bunch of HighEnd Studio Spot 575 CMY fixtures and noticed the recent addition of Iris Mode parameter.  I added a value to the Home Preset for this parameter, however if I send the fixture home, the Iris Mode doesn't go to it's home value.  WERE YOU USING HOME FROM THE ENCODERS?  THERE IS A KNOWN PROBLEM WITH THIS, WHICH WILL BE ADDRESSED SHORTLY.  THE HARDKEY HOME SHOULD HAVE WORKED PROPERLY (TAKE TO THE HOME PRESET VALUE).
    -One suggestion: When updating presets and pallets, I usually place the lamps in the preset I wish to update, make my changes, and then update the preset/pallet.  What I find at the moment is that I have to enter the preset/pallet number, make the changes, and then enter the number again when entering the update command.  Would it be possible to be able to just type [update preset enter] and have the console automatically post the number to the command line by using the last target that was selected.  At present if I try the [update preset] syntax it will post the last target I updated, not the last one that was recalled from.  I have recently started using the direct selects and this does make it a bit easier, but see point above for why this can be a bit frustrating.  YES.  WE NEED TO ADD A FUNCTION THAT WE CALL "UPDATE LAST MANUAL REFERENCE."  THIS WILL WORK FOR CUES AND MAKE THE UPDATE THAT YOU WANT ABOVE POSSIBLE.
    I'm sure you are probably aware of some of these points already, but I have listed them anyway just incase.  Keep up the great work - I'm loving the new software  THANKS AS ALWAYS FOR THE INPUT.  SORRY ABOUT THE ALL CAPS. ANNE.
    Cheers
  • BrentFJ:
    -Occasionally I get a syntax error when lamping off fixtures.   CAN YOU LET US KNOW THE FIXTURE TYPE?  IS IT HAPPENING WHEN YOU HAVE A MIX OF DIFFERENT FIXTURES SELECTED?  OR JUST ONE TYPE?
    -Trace Trace, which as I understand is suppose to trace an update as far back as possible in the cue list, doesn't appear to be functioning.   TRACE TRACE IS INTENDED TO ADD A NEW CHANNEL.  SO, IF IN CUE 5, YOU BRING UP CHANNEL 1 FOR THE VERY FIRST TIME, AND YOU MODIFY CHANNEL 2, WHICH WAS A TRACKED LEVEL ALREADY IN THE CUE LIST.  IF YOU UPDATE TRACE - CHANNEL 1 IS ADDED TO CUE 5, BUT NOT TRACKED BACK TO CUE 1, WHILE CHANNEL 2 SHOULD BE "TRACED" BACK TO ITS ORIGINAL MOVE.  IF YOU WANT TO "ADD" CHANNEL 1 TO THE LIST, TRACE, TRACE SHOULD DO THAT.  AGAIN, WILL LOOK AT WHEN AT A DESK, BUT THAT'S THE INTENT.
    -Iris Mode: I want the iris mode to change 6 seconds into the cue, so I put a delay of 6 on the iris and iris mode parameters, however the Iris mode is still changing at the top of the cue.  FIXTURE TYPE?  IN GENERAL, MODE CHANGES HAPPEN IMMEDIATELY, AS THEY SIMPLY TOGGLE OTHER BEHAVIOR.  WOULD BE HELPFUL THOUGH TO KNOW THE FIXTURE TYPE.
    -Effects: I have a linear effect running on a group of chans.  the effect is set to cascade - fade by size with a grouping of 7.  On its first cycle some of the chans that are grouped together don't come up, or are slow in coming up.  Subsequent cycles, the chans are coming up when they should be.  CAN YOU EMAIL SHOW FILE, IDENTIFY CUE AND EFFECT YOU ARE LOOKING AT?  (THANKS!)
    -Fader Control - Rate: What is the current situation with being able to speed up or slow down a cue?  Last I heard, rate wasn't working correctly.  Also, how does one affect the rate on the master playback pair?  Do you use the rate softkey under "fader control" or is the master pair constantly set to be a rate override (as far as I can tell the latter is the case, but a bit of info would be useful as this caused a show stop this evening)  AT THE MOMENT, RATE HAS TO ALWAYS BE ASSIGNED TO THE FADER THAT YOU WANT TO TAKE RATE CONTROL OVER.  AND IT IS RESET TO 100% WHEN THE CUE (OR CUE SEQUENCE) IS COMPLETE.  WE WILL HAVE A WAY TO LOCK RATE CONTROL ON A FADER UNTIL LIFTED (1.5).  AT THE MOMENT, [RATE] + [LOAD] ASSIGNS THE RATE WHEEL TO THAT FADER. ON ION, THIS IS THE LEVEL WHEEL.  THIS IS WHY ON ION THIS IS TRICKY - ONE WHEEL... MORE ON THIS SOON.  THANKS!!  A
     Thanks once again!
    Cheers
    [edited by: Anne Valentino at 7:25 PM (GMT -6) on Wed, Jun 25 2008]
  • Anne Valentino:
    BrentFJ:
    Hi Anne - Thanks for the reply.  In reply to your reply....
    YEP, AT THE MOMENT, REM DIM IS JUST  A TOGGLE STATE.  YOU CAN'T ACTUALLY MAKE CHANGES TO VALUES AND THEN REVERSE THE REM DIM MODE.  WE'VE DISCUSSED CHANGING THIS, BUT WERE HOLDING OFF UNTIL WE COULD EVALUATE HOW HIGHLIGHT/LOWLIGHT MIGHT IMPACT HOW PEOPLE ARE TRYING TO USE REM DIM.   That makes sense.  FYI - I prefer to use highlight.  Ended up trying rem-dim due to the glitches mentioned before in hightlight.
    IN WORK.  LOOKING TO LOCK ANYTHING POSTED IN THE CIA, SO THAT IF YOU DO SOMETHING THAT NEEDS TO BE POSTED TO THE CIA, WHAT YOU HAD BEFORE COMES BACK WHEN YOU CLEAR THAT STATE.  Smashing!
    YEP.  WE CHANGED THE CODE IN 1.3 SO THAT UPDATE WOULD NOT ADD ANYTHING TO A REFERENCE UNLESS SPECIFICALLY REQUESTED.  THAT WAY, YOU COULD HAVE A BUNCH OF MANUAL STUFF ON STAGE AND NOT WORRY ABOUT GETTING UPDATE INTO A SINGLE REFERENCE BY MISTAKE. SO, IF YOU WANT TO ADD IRIS, EDGE AND FOCUS, YOU HAVE TO SPECIFY THAT.  [IRIS, EDGE FOCUS UPDATE TARGET] Makes sense - thanks for the clarification
    -I have a bunch of HighEnd Studio Spot 575 CMY fixtures and noticed the recent addition of Iris Mode parameter.  I added a value to the Home Preset for this parameter, however if I send the fixture home, the Iris Mode doesn't go to it's home value.  WERE YOU USING HOME FROM THE ENCODERS?  THERE IS A KNOWN PROBLEM WITH THIS, WHICH WILL BE ADDRESSED SHORTLY.  THE HARDKEY HOME SHOULD HAVE WORKED PROPERLY (TAKE TO THE HOME PRESET VALUE).  I was using the home hardkey.  Syntax entered was [chs] {iris} {iris mode} [home][enter]
    YES.  WE NEED TO ADD A FUNCTION THAT WE CALL "UPDATE LAST MANUAL REFERENCE."  THIS WILL WORK FOR CUES AND MAKE THE UPDATE THAT YOU WANT ABOVE POSSIBLE. Fantastic
     Thank-you very much for the speedy response!!
    Cheers
  • Anne Valentino:
    BrentFJ:
    -Occasionally I get a syntax error when lamping off fixtures.   CAN YOU LET US KNOW THE FIXTURE TYPE?  IS IT HAPPENING WHEN YOU HAVE A MIX OF DIFFERENT FIXTURES SELECTED?  OR JUST ONE TYPE? one type of fixture - Studio Spot 575 CMY.  The syntax i usually enter is [chans 3 > 5 enter][more sk][lamp ctrls][lamp off].  Sometimes I get the syntax error, sometimes I don't.  Work-around is [select last][lamp off].  Haven't recieved any syntax errors when using select last.
    -Trace Trace, which as I understand is suppose to trace an update as far back as possible in the cue list, doesn't appear to be functioning.   TRACE TRACE IS INTENDED TO ADD A NEW CHANNEL.  SO, IF IN CUE 5, YOU BRING UP CHANNEL 1 FOR THE VERY FIRST TIME, AND YOU MODIFY CHANNEL 2, WHICH WAS A TRACKED LEVEL ALREADY IN THE CUE LIST.  IF YOU UPDATE TRACE - CHANNEL 1 IS ADDED TO CUE 5, BUT NOT TRACKED BACK TO CUE 1, WHILE CHANNEL 2 SHOULD BE "TRACED" BACK TO ITS ORIGINAL MOVE.  IF YOU WANT TO "ADD" CHANNEL 1 TO THE LIST, TRACE, TRACE SHOULD DO THAT.  AGAIN, WILL LOOK AT WHEN AT A DESK, BUT THAT'S THE INTENT. That was the kind of situation I was trying (i think??)  If adding a new chan will TRACE TRACE track back to the start of the cuelist or only back to the next block?  I was trying this half way through a cue list and the chan only traced back until it reached a block.
    -Iris Mode: I want the iris mode to change 6 seconds into the cue, so I put a delay of 6 on the iris and iris mode parameters, however the Iris mode is still changing at the top of the cue.  FIXTURE TYPE?  IN GENERAL, MODE CHANGES HAPPEN IMMEDIATELY, AS THEY SIMPLY TOGGLE OTHER BEHAVIOR.  WOULD BE HELPFUL THOUGH TO KNOW THE FIXTURE TYPE.  Studio Spot 575 CMY.  So I'm assuming the work around to delay the mode change would be to make a new cue with the change there and have it follow/hang from the previous cue? To add to this as well, It doesn't seem possible to alter variable speeds in the Iris Mode.  eg IRIS RAMP OPEN - it is not possible to alter the speed of the ramp open.
    -Effects: I have a linear effect running on a group of chans.  the effect is set to cascade - fade by size with a grouping of 7.  On its first cycle some of the chans that are grouped together don't come up, or are slow in coming up.  Subsequent cycles, the chans are coming up when they should be.  CAN YOU EMAIL SHOW FILE, IDENTIFY CUE AND EFFECT YOU ARE LOOKING AT?  (THANKS!) Showfile to follow shortly...
    -Fader Control - Rate: What is the current situation with being able to speed up or slow down a cue?  Last I heard, rate wasn't working correctly.  Also, how does one affect the rate on the master playback pair?  Do you use the rate softkey under "fader control" or is the master pair constantly set to be a rate override (as far as I can tell the latter is the case, but a bit of info would be useful as this caused a show stop this evening)  AT THE MOMENT, RATE HAS TO ALWAYS BE ASSIGNED TO THE FADER THAT YOU WANT TO TAKE RATE CONTROL OVER.  AND IT IS RESET TO 100% WHEN THE CUE (OR CUE SEQUENCE) IS COMPLETE.  WE WILL HAVE A WAY TO LOCK RATE CONTROL ON A FADER UNTIL LIFTED (1.5).  AT THE MOMENT, [RATE] + [LOAD] ASSIGNS THE RATE WHEEL TO THAT FADER. ON ION, THIS IS THE LEVEL WHEEL.  THIS IS WHY ON ION THIS IS TRICKY - ONE WHEEL... MORE ON THIS SOON.  THANKS!!  A This is still not consistent with the current behavior.  Enabling rate on the master pair, the wheel does not make any changes to the rate.  Is the master pair FADERS suppose to override cue transition at the moment, as this is the behavior I am seeing...
    Thanks muchly!!
    Cheers
  • Trace trace, just adds a new channel?  So I don't think of the channel as tracking at zero?  Does Trace trace go to the blocked cue or throughout the show.  Granted I don't have a board in around me these days, but I would want the trace trace to be on through the whole show, like run lights that I forgot to program in.  To add the clouds in Scene five that I forgot I'd want to put the clouds in at a level, or fix the cyc for that scene and update trace, expecting, even if its a new channel, to go to the blocked cue and stop, without having to go to blind and find where the first cue that of the scene is.  Am I understanding this right?
  • Hi Jay
    Don't mean to be rude, but I'm struggling to understand what you are trying to say in your post.  Any chance of getting a clearer explination?
    Cheers
  • not rude, it's confusing perhaps.
    Cue 1-3 is preset.  Cue 5-20 is scene 1.
    Cyc is lit in scene 1.  While in cue 15 I forgot that I had added a cloud template (channel 101 which was previously out) and want it to be in scene 1.  I put it at the level that I want it and I want it through that scene.  I update trace the new channel in.  It should add that channel into the block and to the next block.
    I also have put run lights through the board and need to cue them in.  I put channel 300 @ 20 and update trace trace to put them into the entire show ignoring blocks.
    This is what I think should happen.  Is this true?  Like I said i don't have a light board in front of me these days.
    Jay
    [edited by: Jay at 9:38 AM (GMT -6) on Fri, Jun 27 2008]
  • And then I remembered that it runs native on Mac OS (thanks) and I checked.  Trace trace, just goes into the block on a new cue, not past.  I feel like it does the exact same thing as trace does, only with a channel from zero, that seems poor.  If I changed my whole cyc in cue 18 to accomodate the new clouds (101) I should update trace and the whole scene should've changed.  Now I need to go back and figure out where 101 is supposed to go in, like the olden days.
     Again sorry for the confusion.
    Hope this helps.
    Jay
  • Jay,
    On the occasions, that I've wanted to put something like running lights throughout the show, not knowwing about trace trace, I've used Update cue x(first cue) thru cue Y (last cue.)
  • Jay:
    Hi Jay
    If you adjust the level on your cyc and then [update trace] the new value should be applied backwards through the cuelist to the last move instruction or the last block.
    I've tried using [trace trace] and my understanding is if you are bringing up a channel for the first time in the show, lets say in Q20, and you want to update this to be in from the start of the show, update trace trace should trace the update back to the start of the cuelist.
    Is anyone from ETC able to shed some light on exactly how [trace trace] functions...?
    Also, as BSmith posted, if you want to update a chan for the entire show, or a large chunck of the show, ]update cue n thru n] works a treat!
    Cheers
  • The story about trace....
     Right now, in 1.4.1, [Trace] and [Trace] [Trace] work as follows.
    If you are (for example) in cue 5.  You make a change to a light that was in a tracked state (and lets say that this channel received its move instructions in Cue 2) and you add a light that was not previously used (new channel, not included in the cue list up until this stage).  If you [Update] [Trace] - the tracked channel will be modified all the way back to the source of its tracked value (Cue 2) and the new channel will be stored as a move instruction in cue 5.  If you wanted to add that new channel all the way back to the beginning.... [Trace] [Trace] will do that.  So, that new channel would now appear as a track, with a move instruction in your first cue.
    Make sense?... somewhat useful.
    Moving on... in 1.4.2 (due end of month), we will treat a tracked zero (the light is off), just like we would treat a new light.  So, if a light has been inactive (zero) and you want to turn it on, and you want the fact that it is now on to go back through the cue list to the place that you turned it off... you'll do that with [Trace] [Trace].
    Trace works in live recording, and it can also be appended to a channel instruction in blind.  With all things tracking related, if this is confusing for you, I'd recommend you go into blind spreadsheet and play around with trace, trace trace, cue only/track to make sure you fully understand how the data is being impacted.
    Hope this helps guys!
  • Brent... as a follow on... we've tracked down the effects problem (as you know).  Thanks so much.
    Regarding Highlight.  This function is now working to spec.  And the way it currently works is something of a jump ball --- which we debated quite a bit.  When you are in highlight mode, whenever you deselect a channel, the changes that you made to it are manually maintained, but the remainder of the light returns to its non highlight state.    The alternative is to leave channels in highlight as you add new ones.  But, if your intensity highlight state is full (the default), if we leave the highlight state on... you'd need to manually return to a lower level to isolate the next fixture you are working with.
     The best way to get the behavior you are looking for is to select all of the channels that you want in highlight mode, and then by hitting next/last, work with each individually.   Does that make sense?
    a
    [edited by: Anne Valentino at 11:04 AM (GMT -6) on Tue, Jul 01 2008]
  • Hi Anne.
     Thanks for the info on Highlight and Trace Trace. All makes good sense
    Cheers