Running Ion as Eos Backup CH number problem

Hi Questions re Ion Running as Eos Backup

Eos running as Master Ion running as backup consols networked to ETC net3 gateway  CH number 999 outputting on stream 4 address512 in the About screen on the Ion for CH999 it said DMX disabled and we had a loss of output. Patching the CH999 down to CH300 fixed the problem.

Ion 99,999 CH console any idea's ???????

Cheers

Smiley

Parents
  • With mis-matched output limits between Primary and Backup, the lowest count is used. Addresses are output based on channel number, so the patch of Channel 1 has priority, then on to channel 2, 3, etcetera, up until the end of the patch or the address limit is reached.

    As such, if you have more addresses patched than the Ion supports, you might indeed see this behaviour - moving the channel to a lower range causes its patch to be output (but probably something else to not be). 

    -luke-

Reply
  • With mis-matched output limits between Primary and Backup, the lowest count is used. Addresses are output based on channel number, so the patch of Channel 1 has priority, then on to channel 2, 3, etcetera, up until the end of the patch or the address limit is reached.

    As such, if you have more addresses patched than the Ion supports, you might indeed see this behaviour - moving the channel to a lower range causes its patch to be output (but probably something else to not be). 

    -luke-