D1 Driver working with ArcMesh or not?

We purchased about 45 D1 Drivers and the recessed Arc1 fixtures.  The plan was to use WIFI Arc Mesh to control them and wired DMX for the other fixtures.  However there is not an antennae on the D1.  Are there two types of D1?  Wired and Wifi?  How can you tell the difference? 

Thanks

Parents Reply Children
  • Chris,

    Can't seem to get anyone on the phone today, even you....... Hope LDI was grand!

    The question is really, why does this circuit in particular have to be UL 924 when there are other circuits in the room that are UL924?  Does every Emergency Circuit have to comply with UL924? 

    What about the Arc 4 cell fixtures?  why cant we just put those on the Debc and obey the 924?

    Tell me about the 700w driver for the arc lamps?  They are on the Debc too, won't that cover the 924?

    We plan the rig shown on page 15 of the link you sent. 

    Thanks,

    Paul

  • Hi Paul, This is a complicated answer so here is my best run at it.

    The question is really, why does this circuit in particular have to be UL 924 when there are other circuits in the room that are UL924?  Does every Emergency Circuit have to comply with UL924? 

    Every circuit used for Emergency lighting will have to comply with UL924.

    What about the Arc 4 cell fixtures?  why cant we just put those on the Debc and obey the 924?

    I am also a little unclear on this and it is possible this comes down to the AHJ, Authority having jurisdiction, in the end. I recommend the use of Emergency (UL924 rated) ArcSystem Pro fixtures to remove interpretation and configuration of setup from whether the system will be approved or not.

    Tell me about the 700w driver for the arc lamps?  They are on the Debc too, won't that cover the 924?

    The same rules that apply to the Four Cell fixtures apply here. The DEBC will do the work, but you may run into complications with the AHJ on whether the driver needs to be UL924 or not.

    I hope this helps, it is a complicated topic and the NEC changes every three years.

  • Matt

    This helps a lot, thank you.  It’s nice to hear from you again.

    In the last few days I have had several conversations with Jason Perry from the New York Office.  He has been fantastic in answering questions and picking up the phone.  He is in process of arranging swap out of the drivers for emergency service drivers.  

    I will find out who the AHJ is on this project. 

    Are you saying that the 4 cell fixtures have a version that is Emergency too?

    What about the emergency lighting that is already in the room but not on the upgrade list?  We have several incandescent fixtures in strategic locations ( set by an AHJ of the past ) linked to the ELTS.  I was under the impression that we were leaving those circuits as is.  How does that affect the UL 924 ? 

    You are correct.  This is a complicated topic. 

    Thanks,

    Paul