Blinking led house lights

The facilities director switched the house lights to the led version of par 38 bulbs, if I buy evl10 dimmers will that fix my issue with blinking bulbs?

Parents
  • Not necessarily.
    We might be able to figure this out, but I need to ask a bunch of questions
    -Can you describe the specific blinking you are seeing? Is it all the time, only at specific values, only when their levels are moving through a specific range?
    - What are they currently connected to (Sensor ( what type), Unison ( what type)?
    - How many per circuit?
    - Do they all blink or just some of them?
    - Can you provide any more information on the bulbs? Such as:
    - Brand
    - Are they dimmable?
    - If dimmable, are they designed to dim via forward or reverse phase dimming?

    This will help us on the way to figuring it out.
  • We have a sensor sr48 rack, 3phase 4 wire 50/60hz 100,000a 240vac
    With a unison CME Control
    3-6 bulbs per circuit
    Blinking occurs as bulbs go bad, about one bulb per month over 16 circuits
    Bulbs blink when on at any range
    Ecosmart bulbs, rated for 120vac 60hz, dimmable